10-11-2012, 01:11 PM
Hi all

i have a fault with art cool gallery.

unit was running in heating then fan stopped, louvres stayed open as does the fascia.
operation (green) light constantly flashing with no 3 second pause

had a look about but cant seem to find any info

any advice will be greatly appreciated as her indoors is moaning like a good un !!

Cheers Dan

monkey spanners
10-11-2012, 01:50 PM
Does fan run in cooling or fan only mode?

Could be low on charge and fan off due to coil temp being too low, or even coil temp sensor faulty which i've had on LG wall mount.

install monkey
10-11-2012, 02:26 PM
to add to monkeyspanners diagnosis Check Indoor TH.
- Measure resistance of TH.
(air : about 10k Ω at 25 °C,
pipe : about 5k Ω at 25 °C) also check the soldered connections too! haha

dangcornish
10-11-2012, 02:39 PM
thanks for the reply,
problem solved, lost neutral onto pcb
drop of solder job done.
back in the good books with her indoors...........pub!!

install monkey
10-11-2012, 02:43 PM
typical lg fault codes!! :D
thanks for the reply,
problem solved, lost neutral onto pcb
drop of solder job done.
back in the good books with her indoors...........pub!!