PDA

View Full Version : Samsng error 458



pmusikman
25-10-2012, 08:54 PM
Hello,
My MH026FWEA display shows error E559 (outdoos error). My outdoor unit MH060FXEA3A display shows error E458. I think this error is about "outdoor unit fan error". I checked and the fan is working. What could be the problem?
Thank you (I'm portuguese, sorry my english).

Best Regards
Rogério

install monkey
25-10-2012, 09:09 PM
458 Oudoor unit Fan Error or CT1 over current error ODU DVM, FJMFJM Plus/PlusA : Fan errorDVM Plus3, DVM plus2 : CT1 over current error
probably fan motor failing

pmusikman
25-10-2012, 09:52 PM
Thank you install monkey
So you sugest i replace de motor?

install monkey
25-10-2012, 10:07 PM
i cant find any service manuals as its a spanish version, trying to find contact details

install monkey
25-10-2012, 11:16 PM
Q3AnalysisStep 1
Contents
While using cooling or heating, System Turn off and display E458 Error codeCheck point RemarksE458 Error is related with outdoor unit fan Error.Especially, If system have a some problem in fan, in heating mode , it will be happened.And In auto address setting, without pipe checking operation must be happened it.Check to outdoor fan operation.Step 2 If outdoor fan operation is clear, start to pipe checking operation.GuidanceWhen Auto address setting is finished without pipe checking operation, in heating mode, outdoor unit refrigerantdistribution control is malfunction.It make our system to confuse it’s condition.But, basically this error code is concerned about fan error.

pmusikman
26-10-2012, 09:44 AM
Thank you instal monkey.
Can you send me the english version of the manual, please?

pmusikman
26-10-2012, 05:53 PM
Does anyone can please provide me the service manual for MH060FXEA3A?
Thank you.

install monkey
26-10-2012, 09:19 PM
http://www.mediafire.com/view/?u8ppwta0250f6b3

pmusikman
20-11-2012, 10:03 AM
Hello,
Thank you Install monkey.
The malfunction was due to a gas leak.
Aftfer a gas charge, the air conditioning is working fine.

Best regards,
Rogério