Hi all,
Does anyone have any info on an APAC S35, split ducted system? It's a superceeded model on R22? I'm after the refrigerant base charge for one curcuit? Cheers!

cool_tech
23-10-2012, 04:55 AM
Hello,
I haver looked at an apac package unit which is 17 kw. It has a charge of 4.9 kgs R22. hope that helps. you will have to allow refrigerant for pipe run.

Watto
23-10-2012, 11:17 AM
Thanks, have a great day!

Mick13
24-10-2012, 04:45 AM
i recently repaired a gas leak on an s25, it was a 2 stage unit with 3.8kg per stage. i imagine each stage in yours will take about 5kg. In fact, cool_tech mentioned an s17, the s35 is likely close to 2 s17s together (ie 2 stages), due to s17 being 17kW and 2 x 17kW = 34kW (close to s35).

do this though, there is a sticker on the outside of the unit where the ref. charge will be blank, however i think on those units there is another one inside the electrical panel with the info you are after.