PDA

View Full Version : Vac pump on suction or discharge valve



xan2282
19-10-2012, 09:19 PM
Hi

To create vacuum inside the compressor I was wondering if it is best to connect the vacuum pump to service valve on suction valve or service valve on discharge valve ?

Or will it give the same result no matter which one I connect it to...

How long time do I have to run the vac pump to make sure all air is out of the compressor housing.

Thank u......

install monkey
19-10-2012, 09:30 PM
vac on both sides for as long as possible, a torr gauge should be used to reach 500 microns or under 3 torr

xan2282
19-10-2012, 10:01 PM
OK thanks.

But about these 2 service valves. Are they both connected to the inside of the compressor housing ? (Bitzer comp)

It they are, then I guess it should be enough to vac. from only one of them.

Or are the not having suction from the same area inside the compressor ?

chemi-cool
19-10-2012, 10:13 PM
There are valves inside the compressor, remember?

glenn1340
20-10-2012, 01:39 PM
If there are two service valves why not connect to them both? You`ll increase the vacuum flow and cut down the evacuation time.