13-10-2012, 08:26 AM
Dear Friends
I have a problem in selectingan evaporator coil for a fish storing cool room which maintains at -20 Deg C. Thecooling load is 14.4 kW/hr, Te -26 Deg C. The evaporator manufacture catalogue givesRefrigeration capacity 14.3 kW/hr @ 6KTD, Cooling surface 85 M³ with 3 x 450 W fans and defrost heater load of 12 kW.I am confident that if I select this, the FCU load, correction factor, KTDadjustment which needs for fish at 4, fans & heater loads are not accountedfor. Is it necessary for me to select a higher capacity evaporator taking intoconsideration all miscellaneous loads? Once adjusted to remove all miscellaneousheat loads discussed above needs a capacity of 29.8 kW @ 6KTD evaporator modeland finally it gives 15 kW/hr. Please give me an advice on this subject.
I have a problem in selectingan evaporator coil for a fish storing cool room which maintains at -20 Deg C. Thecooling load is 14.4 kW/hr, Te -26 Deg C. The evaporator manufacture catalogue givesRefrigeration capacity 14.3 kW/hr @ 6KTD, Cooling surface 85 M³ with 3 x 450 W fans and defrost heater load of 12 kW.I am confident that if I select this, the FCU load, correction factor, KTDadjustment which needs for fish at 4, fans & heater loads are not accountedfor. Is it necessary for me to select a higher capacity evaporator taking intoconsideration all miscellaneous loads? Once adjusted to remove all miscellaneousheat loads discussed above needs a capacity of 29.8 kW @ 6KTD evaporator modeland finally it gives 15 kW/hr. Please give me an advice on this subject.