View Full Version : maneurop specs
cadwaladr
11-10-2012, 01:17 AM
can anybody tell me the spec of a maneurop condensing unit model number mgz040c12e the horsepower is what i need and is it hbp/lbp/mbp thanks.
chemi-cool
11-10-2012, 05:51 AM
compressor on that unit is MTZ40, horse power is 3.5
They dont make blue star anymore, now they are called optyma.
Grizzly
11-10-2012, 05:58 AM
I have similar data as per Chemi.
The Dean and Wood catalogue. Pages 49 and 50.
The new code is MGHD060HPC12E which is listed as 3hp 3ph?
Best check with D&W Tech services!
chemi-cool
11-10-2012, 05:10 PM
Grizzly, MGH is for high ambient with MINERAL oil and compressor on that unit is MT36.
The letter Z indicates POE oil.
Depend of the refrigerant you use, [suitable for 134,404,507,407,22,12] it will go down as -40C evap. temp to 10C evap. temp.
I use them for milk cooling at 0C evap and freezers at -30 evap.
cadwaladr
11-10-2012, 06:48 PM
thanks guys