23-09-2012, 04:48 PM
is there any thumb rule for the no of rows for chilled
Water
or dx cooling coil in ahu
Brian_UK
23-09-2012, 11:14 PM
Not that I know of.
nevinjohn
21-02-2013, 08:39 AM
Well, if its dealing with full fresh air, a min of 8 row deep is suggested, and for recirculation type with 10-15% fresh air, go with 4 row deep.
DTLarca
21-02-2013, 08:43 PM
Surely, if it's full fresh air then you want to maximise the bypass factor so as not to over cool the space ?!
If so then reduced rows are called for.
Brian_UK
21-02-2013, 08:49 PM
Shouldn't worry Marc, he's a one post wonder from last September ;)
Although, of course, your observation is valid.
DTLarca
21-02-2013, 09:07 PM
Brian, I guess it would also depend on occupancy numbers versus load. The higher the occupancy the greater the BPF required. A low occupancy but with a high load would indeed mean more rows required if one wanted smaller ducts and fan i.e. low air volumes.