01-01-2006, 06:13 PM
Hi

Hoshizaki ice flaker not producing.

Will be looking at this problem next week,the info I have is as follows.

Condenser fan runs
Water tank full
Compressor not operating

On the control board there is relay K1 which supplies the compressor relay,there is a live into it but none out,if bridged then compressor runs.

Sorry no more details,would appreciate if someone could shed some light so as I can save time on site.

Happy New Year

Bernard

bernard
01-01-2006, 06:27 PM
Hi

Bin switch is ok. Please explain how I would reset it and under what circumstances would I need to reset it.

Regards Bernard

bernard
01-01-2006, 07:33 PM
HI

There no push button and power has been switched on off.

Regards

PAXFREON
01-01-2006, 07:48 PM
bin switch

PAXFREON
01-01-2006, 07:49 PM
is there a reset on the board?? also check for possible blown fuse on board

jamcool
04-01-2006, 01:06 PM
On the hoshizakis i have seen when the unit starts there is water flow for about 3 minutes the first stage is a defrost then after 2 to 3 minutes it starts.the board must be keeping out the comp.or can the relay be changed maybe contacts burnt on relay?

bernard
04-01-2006, 07:20 PM
Hi

I have ordered new board as the relay is not easily changeable.

The Bin switch cuts everything out

Regards

Bernard:)

Steve Wright
04-01-2006, 07:46 PM
Call Danny Moore @ Hoshizaki 770 487 2331

Mark
09-01-2006, 11:35 PM
Hoshizaki uk 08454560585.ask for technical support.