Hi everyone. Could someone please help explain how the setpoint setting works with the KRP4A.
In its data sheet there is a very clear table mapping ohm values to set points. So lets say I set 5 ohms between the terminals which places the setpoint at 17 degrees, so what happens when you change the setpoint manually at the remote controller(thermostat)? Wouldn't that create a mismatch of settings?
I would assume setting the setpoint would mean applying the X-ohm resistance for 1 second then opening the terminal(or disconnecting it). Is this how it should be? Or does the KRP4A only trigger a change in setpoint when you change the resistance (for example placing 6-ohm then 5-ohm will reset the temperature back to 17 after it was manually changed to another setpoint).
Appreciate your help :)
In its data sheet there is a very clear table mapping ohm values to set points. So lets say I set 5 ohms between the terminals which places the setpoint at 17 degrees, so what happens when you change the setpoint manually at the remote controller(thermostat)? Wouldn't that create a mismatch of settings?
I would assume setting the setpoint would mean applying the X-ohm resistance for 1 second then opening the terminal(or disconnecting it). Is this how it should be? Or does the KRP4A only trigger a change in setpoint when you change the resistance (for example placing 6-ohm then 5-ohm will reset the temperature back to 17 after it was manually changed to another setpoint).