View Full Version : Panasonic Inverter CU-S10JKP error kode H11. Help me..any body



fdharmala
20-09-2012, 03:44 PM
Some one can help me.? what is meaning error code H11 and how fixed the problem ?

fdharmala
20-09-2012, 03:48 PM
hello any body ?

install monkey
20-09-2012, 06:53 PM
H11 Indoor / Outdoor abnormal communication
> 1 min after starting
operation
Indoor fan operation
only
• Internal / external cable connections
• Indoor / Outdoor PCB

install monkey
20-09-2012, 06:59 PM
Troubleshooting
When abnormality indication starts again
Is there any wiring error?
• Correct the indoor-outdoor units
connection wires
Check the indoor-outdoor units’ connection wires.
Disconnect terminal 3 wire and measure Vdc between terminal
2 & 3 from the outdoor unit.
Is the Vdc fluctuate between 20-70Vdc?
• Replace outdoor PCB
Reconnect terminal 3 wire and measure Vdc between terminal
2 & 3 from the outdoor unit.
Is the Vdc fluctuate between 20-50Vdc?
• Replace indoor unit PCB.

install monkey
20-09-2012, 07:05 PM
emailed ya the manual- 7meg

frank
20-09-2012, 07:55 PM
hello any body ?

Steady on there fella.....giving just 4 MINUTES before you start shouting for help is a little impatient :eek:

We don't sit on here just waiting for questions you know :D

install monkey
20-09-2012, 08:14 PM
took me 12 minutes to reply- and e mail manual,must be getting old:rolleyes:
also its been over an hour and no thanks,email reply - cant ask for rep points off a new member:D

fdharmala
21-09-2012, 01:28 AM
Troubleshooting
When abnormality indication starts again
Is there any wiring error?
• Correct the indoor-outdoor units
connection wires
Check the indoor-outdoor units’ connection wires.
Disconnect terminal 3 wire and measure Vdc between terminal
2 & 3 from the outdoor unit.
Is the Vdc fluctuate between 20-70Vdc?
• Replace outdoor PCB
Reconnect terminal 3 wire and measure Vdc between terminal
2 & 3 from the outdoor unit.
Is the Vdc fluctuate between 20-50Vdc?
• Replace indoor unit PCB.


Ok thankyou very much for help me. i'll chek the PCB and if i have any problem i'll give news soon.