View Full Version : fujitsu ducted comms error indoor-outdoor



djdg09
20-09-2012, 01:39 AM
i have a fujitsu ducted that has had the error 01 we changed the indoor and outdoor pcb the error is still coming up changed the main pcb on both indoor and outdoor any ideas on why the error is still up do i need to to replace something else as well the pcb i have checked all the fuses. could a relay be fused on the power pcb?

cheers

Tayters
20-09-2012, 02:33 PM
01 is a comms error as you've no doubt sussed out.

Search for Posistor in the forums, should give you some info which may help depending on your unit model number.
Cheers,
Andy.

The Viking
20-09-2012, 03:16 PM
Checked the interconnecting wiring?

If in doubt run a loose cable between the indoor and the outdoor units, I have used extension leads for this in the past.
If it runs on a different cable then you know where the fault is.

:cool:
.

install monkey
20-09-2012, 07:07 PM
01 is rodents nibbled at ur cables- whats the model number?
:p

djdg09
02-10-2012, 12:24 AM
01 is rodents nibbled at ur cables- whats the model number?
:p

the O/D model number is AOT54LJBYL

oldmanriver
02-10-2012, 06:02 AM
Either the Diode Bridge or Active Filter module could be faulty- causing the posistor to open circuit. Also, were the outdoor fan motors tested prior to replacing the Main PCB? If not, they could have damaged the new board. Maybe best to contact Fujitsu Tech Support in your local state office when on site.