View Full Version : daikin cassette FXFQ-M8V3B



yacoub
14-09-2012, 02:35 PM
dear all.
I has been problem with daikin cassette FXFQ-M8V3B it give A3 .
can any person help me ؟
Thanks .

r.bartlett
14-09-2012, 04:03 PM
A3 Indoor Malfunction of drain Level control system

you got a problem with the drain. The pump is running too long and the float isn't dropping down within time..

yacoub
15-09-2012, 09:00 AM
yes, the pump is always running ,
what should i do to solve that problem ?
thanks

r.bartlett
15-09-2012, 11:03 AM
call an engineer?

a/c.king
15-09-2012, 11:38 AM
youve got faulty floating switch,sensor etc......

install monkey
15-09-2012, 04:32 PM
cassette lift pumps on daikins run constantly when in cooling mode and for 1 minute afterwards, either slime /crap in ur drip tray or the drain off the unit is blocked- on the outside of the cassette remove the jubilee clip on the drain - see if it pumps into a bucket, then if this is ok, blow down the drain pipe you disconnected- it may be healthier using compressed air butit gives you a few pointers to check, if the drain is clear and the condensate pump shifts water then the hi lmit float switch may be stuck/jammed- or as a last resort unplug the float plug off the pcb, in uk its a yellow 2 core wire, test continuity on the plug- i have had a float switch fail when all is ok.
yes, the pump is always running ,
what should i do to solve that problem ?
thanks

Palkoper
16-09-2012, 12:23 PM
Check condensate pump and flow switch !!!!

r.bartlett
16-09-2012, 07:06 PM
Check condensate pump and flow switch !!!!

crumbs why didn't anyone else think of that?

frank
16-09-2012, 08:09 PM
I bet it's been many moons since the drain pan was removed and cleaned ;)

yacoub
22-09-2012, 09:20 AM
Thanks to all .
the problem in drain pipe is closed .
we found snake in it .