27-08-2012, 09:16 PM
I arrived to site to find a daikin rsey8kly1 with a l9 fault. Found inverter comp on the way out and need to put system into backup till new comp arrives to site . Any help would be great
Thanks

install monkey
27-08-2012, 09:25 PM
http://www.mediafire.com/view/?6hnxhlb4u4f5fbb
page 58 setting mode 2 on outdoor- disables inv comp

ballvalve
27-08-2012, 09:47 PM
Thanks for that.
I take it that emergency led1 means it disables the inverter comp.

install monkey
27-08-2012, 09:50 PM
yep disables the inverter and just runs the dol comp

install monkey
27-08-2012, 10:02 PM
when u change the inv comp get the oil kit as you need to drain the oil out the dol comp too aswell as the transistor module and diode module /inverter pcb

VRVIII
28-08-2012, 10:55 PM
The oil kit is not required for KL series VRV, they have scroll compressors and a single inverter PCB.