23-08-2012, 04:29 PM
Im getting a surge fault every couple days on this chiller, When it goes down My evap aproach is 7.7 witch wicked high and my condenser aproach is in the negitive, I believe this is a water flow issue but I have no trending ways to prove it. Any sugestiong would help. Thanks

mark957
24-08-2012, 07:04 AM
Controls, the temperature, the flow rate, and the cleaning of the condenser.

goshen
24-08-2012, 10:28 AM
Hi
you should take care of this fast or this will prove very costly !
if when the unit is working your approach is 7 deg !! clean your condenser ,you should also make sure you have the correct water pressure drop across the condenser!