PDA

View Full Version : Angelopo Sm2l Error E2 Please Info About This Error



CHARLIEZOLO
22-12-2005, 04:45 AM
Hi I,m Charlie Zolo If Some One Know About This Error In The Control Panel Angelopo Error :e2 With Bip Bip Thank Yu :)

rbartlett
23-12-2005, 11:11 AM
I have worked on ap stuff in the past..not hugely impressed but there you go. However my mind simply refuses to give up the E2 fault code and I'm pretty sure I don't have any lists. Try

service@angelopo.it <service@angelopo.it>

and they will no doubt send you what you need.

cheers

richard

p.s if they do =come back and post it here ;-)

phil68
23-12-2005, 04:30 PM
Gotta be an evap. sensor fault indication?

CHARLIEZOLO
23-12-2005, 09:37 PM
dear phil68 i did send email to angelopo and they reply for me to change the pcb but i,m not interest to change it have yu or some one els any other idea

phil68
23-12-2005, 10:00 PM
If it's a freezer you're looking at 'E2' on a lot of controllers usually means there's a problem with the evaporator probe i.e. open circuit or out of range. Try checking that the probe connections are secure at the temp. controller terminals. If they are secure you'll have to replace the evap. probe itself.