chico boy
24-07-2012, 08:57 PM
I am having problems with my office split system (SRK35ZG-S). The fault light on the indoor unit flashes 7 times stating that "outdoor fan motor error" i checked out the motor but decided to replace it..new motor fitted and still same problem..The outdoor compressor starts to ramp up but the fan motor fails to start and unit shuts down then flashes the fault lights again....any ideas???

install monkey
24-07-2012, 09:03 PM
outdoor board not powering the fan

chico boy
24-07-2012, 09:25 PM
getting between 256 - 296 v dc at pin connector of pcb

install monkey
24-07-2012, 09:38 PM
timer light flashes 7 times- any flash from the run light- as this can indicate a different fault
http://www.mediafire.com/view/?6rcmr06fcy7bacm
manual is a bit vague- power for fan yes,connector cable ok, condenser fan motor

Andy AC
24-07-2012, 10:37 PM
On the srk 63 they also have a fuse on the underside of the board which is soldered to pcb. If it has gone, you will need to piggyback another fuse on to it to get it to run. Not sure about the smaller machines, but worth a look.

chico boy
25-07-2012, 07:37 AM
Run light on steady...fitted a brand new motor...power getting to pins on pcb (256 -296 v dc)

Airconjon
01-12-2012, 11:12 AM
Fan speed controller fitted ?

Airconjon
01-12-2012, 11:17 AM
Full of gas ?

install monkey
01-12-2012, 12:10 PM
mhi condenser fan motors have a pcb within the motor so you cannot test it. also speed is detected too

Tayters
01-12-2012, 11:40 PM
Run light on steady...fitted a brand new motor...power getting to pins on pcb (256 -296 v dc)

You have a BLDC motor there.
Not sure of the colours but from the 300V DC end, next wire is neutral, then 15V DC to power internal PCB, next is speed input signal, last is speed output.
DC voltage easy to test. I'm not sure on exact values for the speed input and output as I've not checked these myself but I'd imagine you could measure some kind of voltage.
You can measure an AC voltage generated from the fan between the neutral and 300V wires (plug off PCB) when motor is spun.

Ensure power has been off for a few minutes before unplugging motor or the 300V can jump across and cause havoc.