in 22 kw cooling cycle at 0C with bitzer compressor. allways ice formed on compressor body, what ever Ido it is formed again.
how you can advice me to get perfect operation

NoNickName
15-07-2012, 02:55 PM
What did you do exactly?

chemi-cool
15-07-2012, 07:33 PM
super heat too low, liquid boils in pipes and compressor.
What type, if any of defrost?

Sandro Baptista
16-07-2012, 09:08 AM
Yeah, it's liquid going to the compressor.

Check the oil sight glass. The oil is foaming, right?

D.D.KORANNE
31-07-2012, 01:05 PM
Check evaporator ,TEX super heat , evaporator fan direction, partial blocking of evap fins , ice formation etc.

Teuria
23-08-2012, 03:52 PM
Hi

Is that 0C evaporating temp or room/liquid temp? if your room/liquid temp is 0C then you must have evap. temp below that and then your compressor suction side might be littlebit frozen. If evaporating temp is 0C then check superheat.