View Full Version : pump down daikin vrv



gwm121
14-07-2012, 01:52 PM
Pleaase could anyone conversant with daikin let me know if there are any issues with pumpdown on daikin RXY5Q5PA7V1B VRV with 2.3kg added refridgernt in addition to the standard 4.3kg. Saturaday today.. so will phone Daikin Monday,but hoped for quicker answer. Thx.

martinw58
14-07-2012, 04:02 PM
no issues you can pump down the system if this is k series i have manual

install monkey
14-07-2012, 06:29 PM
2hr 10 mins is pretty quick!!

gwm121
14-07-2012, 09:00 PM
thank you martin, would appreciate a glance at manual to see if method is run -turn off liquid, turn off suction when 0.1 psi, turn off power.. or if this model has pumpdown button or software control setting. thx for confiming no issues, hoped that the added 2.3kg was ok to recover but wanted to be sure. thx again for taking trouble to give short concise good answer.

oh by the way when someone is so helpfull as to offer to send a flie here, how is that done..

install monkey
14-07-2012, 09:15 PM
install mediafire and upload the manual-its tricky but saves everyone begging for it!!

martinw58
15-07-2012, 09:00 AM
let me have your email and will send

martinw58
15-07-2012, 05:38 PM
manuals are to big to post so need to be sent by email