PDA

View Full Version : Climaveneta.



spamfish
07-07-2012, 05:28 PM
Hi,
Does anyone have a service manual for a Climaveneta FOCS/LN 1942 chiller. (circa 2005)

I have a fault code "compressor anomaly" that does not appear in the literature. I have tried climaveneta website but I am going round in circles

Many thanks

G

goshen
07-07-2012, 07:28 PM
Hi
compressor anomaly is a fault that is connected to the input from the motor protection module,
there are three
oil level
motor temp
and high discharge temp/
your controller is a w3000 carel
if you mail me i will send you back a manual
good luck

spamfish
28-07-2012, 10:28 AM
Thank you, my email address is loooney@sky.com

goshen
28-07-2012, 09:37 PM
you have mail !!

texanul
29-07-2012, 12:54 PM
You should ckeck the black protection inside the electrical of the compressor .