View Full Version : Carrier chiller 30RWA



Palkoper
07-07-2012, 07:24 AM
Hi fellas anyones had problem with Carrier chiller 30RWA it showed me faultcode on ProDialog 30 and I found leak fix it change filterdrier core and double checked LP transductor and still chiller doesnt work . . . :(


I put 28 Kg of R 407 C and still evaporating temperature is about 8 degree should I charge more or what should check to fix it .


Thanks for any ideas to help cheers .

mark957
07-07-2012, 11:30 AM
Controls the expansion valve ..........

goshen
07-07-2012, 07:40 PM
HI
fault 30 should be a comm loss fault??

PaulZ
09-07-2012, 01:59 AM
Hi Palkoper
When you repaired the leak did you remove all the refrigerant and start with new refrigerant or just top up?
If you topped up this will cause a problem.
Regards
Paul