flyboy3b
05-07-2012, 07:04 PM
i have a fedders 3 1/2 ton heat pump that seems a bit wimpy and id like to get a second opinion on my readings.
r-22
liquid line pressure=225psi (110f)
liquid line temp=97f
subcooling= 13
suction line pressure= 87psi (52f)
suction line temp= 59f
superheat=7
air entering the condenser= 85f
exiting the condenser= 107f
air entering the evaporator= 83f
exiting the evaporator= 61f
rel humidity = 80%
there was a partial burnout a couple years ago during the heating operation and the unit was evacuated, pulled down to 250 microns and refilled. it never seemed quite right after that and it seems to be getting worse. the subcooling is about where it should be but its not putting out alot of cold air. the evaporator coil is clean and air is flowing freely. there is no temperature drop across the filter and everything else seems normal. the suction pressure seems a bit high but i am used to working on refrigeration stuff and do not have alot of experience with ac. am i missing something here or is this as good as it gets?
thanks in advance,
mike
r-22
liquid line pressure=225psi (110f)
liquid line temp=97f
subcooling= 13
suction line pressure= 87psi (52f)
suction line temp= 59f
superheat=7
air entering the condenser= 85f
exiting the condenser= 107f
air entering the evaporator= 83f
exiting the evaporator= 61f
rel humidity = 80%
there was a partial burnout a couple years ago during the heating operation and the unit was evacuated, pulled down to 250 microns and refilled. it never seemed quite right after that and it seems to be getting worse. the subcooling is about where it should be but its not putting out alot of cold air. the evaporator coil is clean and air is flowing freely. there is no temperature drop across the filter and everything else seems normal. the suction pressure seems a bit high but i am used to working on refrigeration stuff and do not have alot of experience with ac. am i missing something here or is this as good as it gets?
thanks in advance,
mike