28-06-2012, 06:37 PM
Gents,
How can anyone identify whether the refrigerant supplier has supplied genuine refrigerant
R404a?

Please help me.

Rob White
28-06-2012, 06:53 PM
.

Use the pressure temperature relationship test.

At any given temperature the refrigerant will be at a certain pressure.

Measure the temperature of the cylinder, measure the pressure of the
cylinder and they should corrispond with what it should be on a chart
or comparitor.

Regards

Rob

.

cadwaladr
01-07-2012, 10:11 PM
thats the only way i know,why do you ask the question if you doubt your supplier find another not worth the risk!!

install monkey
01-07-2012, 10:33 PM
http://www.sanwatsusho-global.com/product/pdf/ta_400a.pdf
refrigerant identifier;)

basilyousuf
02-07-2012, 09:59 PM
normaly for cooling down to 0C. the suction pr = 50, discharge pr = 300 psi.