View Full Version : carrier 30rb262 flow switch
goshen
28-06-2012, 07:37 AM
Hi
the unit has a thermal flow switch ,can this input be bridged
for some reason there is a resistor in series to this input
thx for any feedback.
9074
HVACRsaurus
28-06-2012, 11:06 AM
Hi,
The flow switch signal is connected to Digital Input CH15b. To bridge it out connect a plain wire jumper between +C to*CH15b. The 24VAC connections on 11 & 12 will no longer be required.
It's a different chiller but the link below shows a similar flow switch with contacts between the terminals as listed.*
http://www.electvillage.com/up06/up/30gk085-detailed%20wiring%20diagram.pdf
Provided this works, a traditional paddle style or differential pressure type of switch with voltage free contacts fitted between +C & CH15b should work fine.
goshen
02-07-2012, 07:39 AM
Hi saurus
thx for your reply ,all is up and working !!
best regards
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.