would anyone of you technical experts out there have an idea on the maximum operating temp of R22 and R410A say if the ambient temp were to get to 55 degrees C your input would be most welcome :)

chemi-cool
27-06-2012, 07:27 PM
Been to 50C, hard to breath, burn your lungs, cooling units just running, you'll have to wait and see, I think they will survive it, just.

Brian_UK
27-06-2012, 11:39 PM
Check a PT chart for temp/pressures.

Check MSDS sheet for critical temperatures.

pyro45686
28-06-2012, 01:23 PM
itd be getting pretty close to your HP cut out i think. R22 lines up to 1840kpa at 50*c on my PT chart and r410 lines up with 2960kpa at 50*c. and condensing temp need to be higher by at least (?)15*C(?) on top of ambient so you get a plenty of liquid

Rob White
28-06-2012, 06:47 PM
.

Most air cooled systems are sized to have about 15 degC temp differance
above ambient temps.

So if the ambient was at 40 degC the the condensing temp would be about 55 degC.

The critical temp for R22 is 96 degC and R410 is 74degC.

On paper that reads as 81 degC and 59 degC respective ambients.

But the ststems would not tolerate that.
It is higher than EN 378 pressure test standards for those refrigerants.

I would say R22 does not want to be much above 22barg or about 40degC
and R410A does not want to be above 34 barg.

But as others have said they may run higher.

Regards

Rob

.

al
28-06-2012, 09:17 PM
Si

Get the Bitzer app for your phone, as Rob says critical temps are very close to your ambient, there is bugger all you can do about the temperature but it would be feasible to replace the charge when it cools down, at those temps you must have issues with refrigerant breakdown?

Al