View Full Version : pressure testing



cadwaladr
26-06-2012, 09:41 PM
had a strange one today was pressure testing a 5hp machine to locate a leak,attached nitro to 250psi located leak on the return bend on the condensor brazed it tested again another leak on another bend brazed it tested again you guessed it another one now the leaks did not appear to show on original test,this machine is on 404a so it runs in excess of 250 psi guess a new condensor needed?

install monkey
26-06-2012, 09:48 PM
scrapyard time!

jdunc2301
26-06-2012, 09:59 PM
had this before mate, 7 of the buggers, gave up in the end and lets have a new coil!

Goober
26-06-2012, 10:37 PM
The extra leaks will be your own doing...unwittingly...it'll be the heat from the brazing of one leak weakening the copper/welds. Copper can be very thin on the bends of condensers as gets stretched thin when being bent. Always wondered why more care, by manufacturerers, not taken here as this is where we get the highest pressures...

cadwaladr
26-06-2012, 11:00 PM
The extra leaks will be your own doing...unwittingly...it'll be the heat from the brazing of one leak weakening the copper/welds. Copper can be very thin on the bends of condensers as gets stretched thin when being bent. Always wondered why more care, by manufacturerers, not taken here as this is where we get the highest pressures...uhm maybe but the leaks were about 2foot away from each other? and i was only verrrry low heat.

install monkey
26-06-2012, 11:06 PM
lennox coils were renoun for failing- think they were made out if copper coated foil!-but scrap yards arent fussy
had a daikin coil fail on the middle of the coil-blobbed it all ok

Yuri B.
28-06-2012, 06:46 PM
Hello. They should've been there all the way. Just the biggest of them catched your eye first; then after that was brazed, the "next size" came forward most noticably, and so on.

BKTP
21-08-2012, 02:27 PM
uhm maybe but the leaks were about 2foot away from each other? and i was only verrrry low heat.

Ok try this, take a 2 foot piece of copper tubing any size you have handy, hold one end with a bare hand and hold the other to just a candle flame (much less btu's than torch). Count how long you can hold. You will then understand the physics of coppers conductivity. Without heatstop compound or at least a wet rag you could well be creating the domino effect you are experiencing.

Fixaman
21-08-2012, 09:55 PM
Ok try this, take a 2 foot piece of copper tubing any size you have handy, hold one end with a bare hand and hold the other to just a candle flame (much less btu's than torch). Count how long you can hold. You will then understand the physics of coppers conductivity. Without heatstop compound or at least a wet rag you could well be creating the domino effect you are experiencing.

Oh please get a grip

Fixaman
22-08-2012, 12:23 PM
had a strange one today was pressure testing a 5hp machine to locate a leak,attached nitro to 250psi located leak on the return bend on the condensor brazed it tested again another leak on another bend brazed it tested again you guessed it another one now the leaks did not appear to show on original test,this machine is on 404a so it runs in excess of 250 psi guess a new condensor needed?You would of found it if you had been testing at the correct pressure for the high side @ 360 psi, prv's permitting.

martinw58
22-08-2012, 07:11 PM
had this befor if the copper is pitted you end up chasing leaks