View Full Version : carrier vector 1500 high pressure 410 psi
akisskam
25-06-2012, 10:58 PM
hi from greece.i have a vector 1500 and he works with 50 psi low pressure and 410 the high pressure .any ideas about that .the temp go down very slow .the out temp is 38c celcious.thank.
cadwaladr
25-06-2012, 11:12 PM
clean the condensor and take the front doors off.
akisskam
26-06-2012, 11:05 PM
i do it and nothink change .maybe if i dont make good vacum in system.how can i do it?thanks.
akisskam
26-06-2012, 11:07 PM
have anyone a manual for this unit.thanks
cadwaladr
27-06-2012, 12:00 AM
has this unit got any history of being recharged recently if yes then it may have been wrongly charged,recover gas and vac it for 24 hours and recharge to the amount on the data plate[in liquid only,what happens when you put it thru a pretrip?
akisskam
27-06-2012, 05:26 PM
he has one fault a127 check sct sensor .the fault doesnt clear
akisskam
27-06-2012, 05:35 PM
this is not active fault
jday_michel
29-06-2012, 03:44 PM
I have a 1550 manual vector.
mcnc6@msn.com
jday_michel
29-06-2012, 03:55 PM
9076
thanks
akisskam
02-07-2012, 01:25 AM
thanks so much