Does anyone know how to reset the hours run on the ssm controllers and do you need a password.
Grizzly
14-06-2012, 08:20 PM
Does anyone know how to reset the hours run on the ssm controllers and do you need a password.
Hi redroge.
I am sure I have it somewhere, can you remember what model chiller it is for?
Grizzly
CV_Geardrive
15-06-2012, 05:17 AM
Hi,
As far as I know there is no SSM controller.
There is SMM and SCM.
In SMM you cannot reset hours and starts.
In SCM you cannot reset hours and starts as standard procedure but you can remove the EPROM and put it again. Then you may have HRD4 alarm and reset hours and starts of ALL compressors but you also have to reprogram the module.
CV
redroge
15-06-2012, 12:42 PM
my mistake its smm on a cgah225 chiller and its coming up with service demand on the screen
saw a van in the states with Grizzly refrigeration on the side! has someone gone multinational.
Grizzly
15-06-2012, 03:02 PM
I wish!
Oviously they make do with the bear minimum!
Hopefully what I have sent you will help.
Grizzly
redroge
15-06-2012, 04:45 PM
Hi grizzly
not recieved anything what info have you got
cheers redroge
Grizzly
15-06-2012, 11:57 PM
Hi grizzly
not recieved anything what info have you got
cheers redroge
Now you have it!
What do you think?
Will it help?
Grizzly
goshen
20-06-2012, 01:59 PM
well did it help??
redroge
20-06-2012, 06:56 PM
Been back today that info dos,nt seem to relate to smm controllers !
Phoned trane to ask what service demand means and they refuse to give any information,anyway the customer is,nt having any more trane chillers as there aftersales is so bad.
Grizzly
20-06-2012, 07:20 PM
Been back today that info dos,nt seem to relate to smm controllers !
Phoned trane to ask what service demand means and they refuse to give any information,anyway the customer is,nt having any more trane chillers as there aftersales is so bad.
I beg to differ what I gave you should work.
Refer to F4, also refer to password lock out F501.
Maybe I did not give you enough.
refer to the attached.
Grizzly
redroge
21-06-2012, 09:14 AM
Thanks grizzly
Could,nt get past Fp will have another go next week when back at work (on a three day week).
redroge
25-06-2012, 05:54 PM
Thanks grizzly
been back to site today all sorted.
Grizzly
25-06-2012, 06:05 PM
Thanks grizzly
been back to site today all sorted.
Glad to be of assistance.