Hi everyone,
Can anyone help me with truck thermoking RD-TLE unit with R404a i charged by weight as written but the unit can not get the setpoint(-21centigrade). any advices or ideas?
Thanks

tspgr
06-06-2012, 06:09 PM
Hello mre212

Give more details ......
outside temp presure readings box dimensions ...

mjreefer
09-06-2012, 02:41 PM
hi the TLE is prone to ice build up so check superheat it is important on this evap because the coil is small, if you cut the yellow wire to evap fan motors they will start in high speed preventing initial ice build up also check air switch setting should be between 0.9 and 1.0 not over 1.0 as this will reduce capacity to much before auto defrost will initiate. you also need to consider what mode the other compartment is in or are you only using one compartment ?

mre212
13-06-2012, 02:24 PM
Hi all and thank you,
I noted that the suction valve solenoid de-energized on cooling mode on both evaporators and i do not have the wiring diagram and the manual for control(THERMO KING THERMOGUARD).so can you send it to me please. This is my e-mail:
r.e951@yahoo.com[/email]
best regards

mre212
01-07-2012, 12:02 PM
Hi evreyone,
if any one has wiring diagram for Thermoking RD-TLE please send it to me i need it as soon as possible
Thanks
Email: r.e951@yahoo.com