View Full Version : Fan speed controller set up
How do you set up a new controller, with adjustable
electronic control.
Brian_UK
06-12-2005, 08:20 PM
How do you set up a new controller, with adjustable
electronic control.If it's a new controller then read the instruction manual.
chillin out
06-12-2005, 09:34 PM
How do you set up a new controller, with adjustable
electronic control.
You adjust the setting to either speed up or slow down the fan.
Chillin:) :)
kengineering
09-12-2005, 01:17 AM
You might try taking amp readings then do the math.Ken
rpbuenaflor
08-01-2006, 03:07 PM
Normaly theres fitted speed regulator controller on it try to read the manufacturer's manual carefully.
rudi
tonto
09-01-2006, 12:36 PM
Guys,
With an adjustable fan speed control, what would be the correct condensing temp to set a fan speed control to regulate the temp to?????
Peter_1
09-01-2006, 08:23 PM
How I do it what won't say this is the correct procedure: I take the estimated HP in summer (10 K above 30°C outside temperature ) and regulate then that the fans are running full speed.
Eventually blind the consensor so that pressure can rise.
Minimum speed is a speed that the fan is still running and can start up alone after a complete standstill (fan must be able to overwin it's bearing friction)
frank
09-01-2006, 08:48 PM
Hi Peter
Most electronic fan speed controllers have a hard start built in so no need for worrying about minimum setting and starting.
The fan normally starts at full speed for a set period and then control takes over.
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.