28-05-2012, 09:32 PM
indoor unit on simplified room controller-pac se51 cra
start up and controller illuminates then after 30 sec dissappears
there is the round dot to indicate power
indoor unit does nothing
indoor 240v input , live to neutral and live to earth neutral-earth 0v
indoor address 111 remote controller address 11
test condensate float swich - open circuit-ok= no water in drip tray
no fault indicated on the g50
there is a vin card on the room for lights but i dont think he ac is controlled off this
20mm glass fuse ok, rh led lit lh led not lit- tried jumper pin swe to try test fan/drainpump- nothing
anything else i could check or plan b swap the board with a spare unit