Hi, <br>Can anyone help me with some advice on a Rhoss chiller? It's model can be seen on the attached pictures.<br>When turning off the chiller manually, the pressure on the&nbsp; discharge side rises from 13 bars to 26 bar for about 10 seconds, and the pressure on the aspiration side remains constantly on&nbsp; about 4 bars and the safety controller ( pressostat) stops turns off the unit. Then the chiller can not be turned on, just after resetting manually the safety controller (marked with red on picture). In auto mode, the chiller does not operates at all. What can&nbsp; be the problem?<br><br><br><img src="http://www.refrigeration-engineer.com/forums/attachment.php?attachmentid=8985&amp;stc=1" attachmentid="8985" alt="" id="vbattach_8985" class="previewthumb"><img src="http://www.refrigeration-engineer.com/forums/attachment.php?attachmentid=8986&amp;stc=1" attachmentid="8986" alt="" id="vbattach_8986" class="previewthumb"><br>The othe problem is with the ELIWELL ECH 210 BP electronic controller. I can't acces it's menu from the keyboard. I<img src="http://www.refrigeration-engineer.com/forums/attachment.php?attachmentid=8986&amp;stc=1" attachmentid="8986" alt="" id="vbattach_8986" class="previewthumb"><img src="http://www.refrigeration-engineer.com/forums/attachment.php?attachmentid=8985&amp;stc=1" attachmentid="8985" alt="" id="vbattach_8985" class="previewthumb">s it password protected maybe ? What can be done?<br><br>Thank you in advance for your help!<br><br>BR<br>

Brian_UK
28-05-2012, 11:12 PM
Source code removed from post....


Hi, Can anyone help me with some advice on a Rhoss chiller? It's model can be seen on the attached pictures. When turning off the chiller manually, the pressure on the discharge side rises from 13 bars to 26 bar for about 10 seconds, and the pressure on the aspiration side remains constantly about 4 bars and the safety controller ( pressostat) stops turns off the unit.

Then the chiller can not be turned on, just after resetting manually the safety controller (marked with red on picture). In auto mode, the chiller does not operates at all. What can be the problem?

The other problem is with the ELIWELL ECH 210 BP electronic controller. I can't access it's menu from the keyboard. Is it password protected maybe ? What can be done?

Thank you in advance for your help!

NoNickName
29-05-2012, 08:09 PM
Which pressure switch trips? LP or HP?

csaba1966
29-05-2012, 08:49 PM
The HP switch

goshen
30-05-2012, 05:22 AM
Hi
try this: http://en.extpdf.com/eliwell-ech-210-bp-pdf.html#a1
good luck

Grizzly
30-05-2012, 06:47 AM
ECH Manual sent to your email address.
Good luck,
What you describe sounds like the chiller is not pumping down but ramping up with no condenser fans running.
Does your condenser fans run?
Grizzly

NoNickName
30-05-2012, 05:53 PM
Condenser fans tripped or ineffective, or too much refrigerant.

csaba1966
30-05-2012, 07:22 PM
Thank for your advices. But the described things happen when I stop the chiller manually - becouse the chiller runs only in manual, the auto mode does not work. Started manually , the chiller runs properly (no problem with fan or refrigerant).
The controller does not react to any key and I can-t access it's menu. There is a remote mounted on the wall- on that can be selected the mode: auto or manual. The unit operates now only in manual mode.

goshen
01-06-2012, 02:23 PM
Hi
it would seem that the unit shuts down on pumpdown and condenser fans stay off,
check your settings .
good luck