View Full Version : charging problem



kefah
26-05-2012, 10:59 PM
i have craft type 2 ton ac window type
during charging i encounter a problem
condenser is separated into 2 separated heat zone
one cold and one hot
so why that is happen

jdunc2301
27-05-2012, 07:22 AM
Let me clarify...your condenser is half hot and half cold?

sedgy
27-05-2012, 04:34 PM
why is this < http// you tube on a website for a/c units ? < = sedgy

tonyelian
27-05-2012, 08:55 PM
hi
there is a restriction there is a small filter at the bottom of the condenser check it

kefah
27-05-2012, 09:02 PM
thank you for your reply

kefah
27-05-2012, 09:04 PM
Let me clarify...your condenser is half hot and half cold?
yes that is what i am meaning

r.bartlett
27-05-2012, 09:04 PM
yes that is what i am meaning

did you weigh the charge in?

kefah
27-05-2012, 09:07 PM
did you weigh the charge in?

yes i weght it

jdunc2301
28-05-2012, 07:29 AM
Restriction then

mikeref
28-05-2012, 08:22 AM
You using the right type of refrigerant? What is the suction pressure?

kefah
28-05-2012, 07:25 PM
can you explain more

kefah
28-05-2012, 07:44 PM
Restriction then

can you explain more

kefah
28-05-2012, 07:45 PM
You using the right type of refrigerant? What is the suction pressure?
yes its right type of refrigerant

jdunc2301
30-05-2012, 07:58 AM
Restriction would mean theres a blockage restricting the flow of refrigerant....if there is a restriction it could technically work like an expansion device as one side of the restriction will be high pressure and the other side of the restriction would be a lower pressure.......thats the best way i can explain what i mean its too early in the morning to get my brain working!

kefah
01-07-2012, 08:12 PM
thank you every one for helping me