25-05-2012, 01:53 AM
got a call yesterday to a holding room 1.5 hp hubbard/prestcold type semi hermetic all the gas r12 had gone traced the leak and repaired it the tev was leaking a termix? [manufacturer so changed it to a danfoss 134a valve and charged it with 134a,the oil will need changing i know and was thinking of vaccing a vessel and pulling the oil from the compressor via the vessel to save removing the comp and then filling with suitable oil.

monkey spanners
25-05-2012, 08:41 AM
That's how I do it, have an old disposable bottle I put extra tap on but a two valve reco bottle would work well. 1.5hp prestcold have 500/600ml oil in them iirc.

monkey spanners
25-05-2012, 09:49 AM
Monkey at work....

http://www.youtube.com/watch?v=thUrX6_SGLI

Oil change on a prestcold plg650.

tonyelian
29-05-2012, 08:33 PM
hi
that is my way empty oil from semi hermetic compressor
take out the lower bolt under winding side
lift it to the back little bit the &that it
u can put the compressor under some pressure for best cleaning

AlexLPD
16-10-2012, 05:45 AM
Very nice video! I had to make a oil change in a maneurop unit, the previous compressor were burn down. And the previous dudes, leve all like thath just changue the compresor, no filter change, no pipe cleaning, no difussor cleaning, or valve cleaning. Now I install a liquid and suction filters, its late to cleaning pipes, but i also change the TXV, the question is... Once i remove the old oil from the compresor, should fill with a litte bit, give it some starts to make sure all the mud and old oil in the carter will be removed, before to fill with the new oil?