when an ac unit is encountering leakage it must be welded and recharges
some times during recharge ablockage in the capillary is happern or in evaporater
so i have to discharge ***** and clean system by r22
so could any body learn why blockage happen
how to evade it
how to open blockage

install monkey
21-05-2012, 09:14 PM
use a vac pump and torr gauge-also purge with nitrogen whilst repairing-good luck:d

kefah
21-05-2012, 09:21 PM
thank you
i made vaccum to the system
by manifold gauge
could explain meaning of torr gauge

install monkey
21-05-2012, 10:23 PM
http://www.google.co.uk/search?q=torr+gauge&hl=en&prmd=imvns&tbm=isch&tbo=u&source=univ&sa=X&ei=r7C6T4RKx9fRBeGmkdUL&sqi=2&ved=0CLwBELAE&biw=1213&bih=488#q=torr+gauge&hl=en&sa=X&tbm=isch&prmd=imvns&bav=on.2,or.r_gc.r_pw.r_qf.,cf.osb&fp=42729e25807455cf&biw=1213&bih=589
pics of torr gauge
you should change your vac pump oil frequently
the gauge indicates moisture level in the system- gauge should be fitted at the farthest point from the vac pump but usually thats not practical- once your gauge drops to less than 2 torr,shut off the pump and you will see the gauge move after 30mins to show moisture is still present in the system. continue vaccing until the gauge stays at 2 torr with the vac pump shut off- if not then add nitro and re vac system- this will remove moisture from the system-good luck

kefah
21-05-2012, 10:29 PM
thank you man

install monkey
21-05-2012, 10:55 PM
http://inspectapedia.com/aircond/Refrigerant_Leak_Repair.htm
found this link that may help