Hi All,


Recently i changed bearing for the pump, when i try to switch it on the power trips. kindly let me know what could cause the problem

chemi-cool
17-05-2012, 02:42 PM
Check the resistance of the between the 3 windings of the motor, it should be the same. if not, you need to rewire or replace the motor.

Mach 2
17-05-2012, 04:53 PM
As chemi-cool states check motor windings but also check that motor and cables are clear to earth and that following the re-bearing job the pump still runs free with no tight spots.
It may be an idea to check that your incoming phases are intact and that the contactor and overload sets are operational.

goshen
18-05-2012, 03:18 PM
Hi
i would make sure the rotor and immpeler are free, and not locked ,before doing anything else !!
good luck

cool_tech
21-05-2012, 10:21 AM
Does this pump run on a vsd?

jason09
30-06-2012, 10:06 AM
is it direct coupled? does it spin by hand?

bratosin
21-07-2012, 07:07 PM
hy. try to change conexion from star to delta. have to work.

texanul
22-07-2012, 10:56 PM
Is it a thermal protection or the fuse is tripping ? If it is a thermal protection is well calibrated ? What kind of pump is it ? Star delta ? Direct start ? More data please !