27-04-2012, 05:31 AM
I need help with a new carrel i33 platform controller I installed with new probes.after verifying all wires connections are correct and the control is programmed correctly, the compressor would not run. After checking wires and settings the compressor would run but with no compressor icon display. And the temp read 10-15 degrees lower the the actuall cabinet temperture on the control. I am thinking I somehow locked the control settings or the control is bad out of the box? And is their a override or correction that can be done ? Any help would be appreciated

chemi-cool
27-04-2012, 09:17 AM
Read this slowly and find where you went the wrong way.
http://www.scribd.com/doc/53319285/carel-ir33-manual

install monkey
27-04-2012, 07:43 PM
carel controllers accept a few types of probes- ntc ,ptc, you prob need to adjust the probe type-see chemi's link

mark957
28-04-2012, 10:31 PM
search the site carel.com

Paul2uall
02-05-2012, 12:02 PM
You can contact Carel UK directly on 020 8391 3540 and ask to speak to their technical help desk.

The IR33 platform uses NTC probes as standard however some models of IR33 can accept other probe types, the range of controllers on the IR33 platform is quite extensive.