View Full Version : Mitsubishi Electric Condensor Fan control



Neddy
11-04-2012, 07:35 PM
Hi Guys I've got a Mitsu unit SUZ-A09. Condensor fan runs on heating mode. On Cooling mode the Condensor coil gets hot and the gas can be heard passing through the unit.Then the fan cuts in for ten seconds cools the coil and the gas noise goes . The same thing happens all over again. Does anyone know what controls the Condensor fan in these units? Should it run all the time?

r.bartlett
11-04-2012, 07:49 PM
probably sog

install monkey
11-04-2012, 07:51 PM
https://rapidshare.com/files/4132394881/SUZ-A09-24VR_Service_Manual__OC304revA_.pdf;
check your outdoor sensors- discharge sensor and coil sensor
also check for flashing lights on the indoor unit

Neddy
11-04-2012, 08:58 PM
Not SOG . I'll check the sensors cheers install Monkey

install monkey
11-04-2012, 09:02 PM
did you get the manual for thermistor values?

Not SOG . I'll check the sensors cheers install Monkey

Neddy
11-04-2012, 09:22 PM
Yes mate cheers.