PDA

View Full Version : Siemens Acvatix SQS65 Actuator



Gary S
23-03-2012, 08:13 PM
Is there an adjustment on these actuators to reverse the direction? i have no info on this valve as im not installing it new. it has only 3 connections. 24v positive and negative and connection for 0 - 10V dc. It is installed on a 3 port valve for heating coil on a AHU.
at the moment when it drives to position 0 it is on full heat where it should be in bypass mode i think. i know a bms engineer would be able to change whether 0vdc is full heat or bypass but if i can do it without calling one out would be handy.
thanks in advance

install monkey
23-03-2012, 08:16 PM
yep theres a lil rotary changeover switch to set the rotation

Gary S
23-03-2012, 08:23 PM
where mate? i was there this evening and couldnt see it anywhere

install monkey
23-03-2012, 08:30 PM
its been modified since i last replaced them, the 0-10v dc signal connects on either y1 or y2 depending on direction req

Gary S
23-03-2012, 08:39 PM
yeah the one i have is different G is 24v positive, GO is 24v negative and Y is the 0-10vdc. then theres R M and U. these are not connected. think R is 0-1000 ohms.

install monkey
23-03-2012, 08:50 PM
dont think there is rotation on a 3 port valve actuator- stem down is 0vdc and 10vdc stem lifts for flow
damper actuators do have the direction switch- cant copy the data sheet for it as its secured

Gary S
23-03-2012, 08:53 PM
no worries thanks anyway. maybe a bms engineer is required to sort it. dont think its been right for a long time

goshen
24-03-2012, 05:56 PM
Hi
mail me, and i will be happy to send you the manual for this actuator,

chemi-cool
24-03-2012, 08:46 PM
https://www.hqs.sbt.siemens.com/gip/general/dlc/data/assets/hq/Electromotoric-actuators-SQS--_10445_hq-en.pdf