14-03-2012, 07:56 PM
gents- city multi ymfc 410a 2007 outdoor address 58,bc 59 indoors 08-13 all present- sw1 1 2 10 on cannot detect 3 parf27 controllers-which are connected on 08,11,13- checked address on controllers-connected on the m net - 108,111,113- system still alarms on 000 6607
run it as a stand alone -disconnected the tb7 for the g50- still alarms- all indoor connections ok, outdoor-29vdc on mnet- swapped o...utdoor boards with another unit-changed address on rotary switches ok-still fooking alarms(have done virgin restart- also the g50 was connected to oudoors 51,58 couldnt detect system 58- refrigerant moniter only showed 51 outdoor 52 bc 1-7 indoors and controllers-couldnt detect system 58- tb7 link from 51-58 ok-mitsi suspect power pack on g50!- any ideas? ta

frank
14-03-2012, 08:35 PM
Fit a Daikin.....self addresses every time :D

AbsoluteWDJ
14-03-2012, 11:01 PM
gents- city multi ymfc 410a 2007 outdoor address 58,bc 59 indoors 08-13 all present- sw1 1 2 10 on cannot detect 3 parf27 controllers-which are connected on 08,11,13- checked address on controllers-connected on the m net - 108,111,113- system still alarms on 000 6607
run it as a stand alone -disconnected the tb7 for the g50- still alarms- all indoor connections ok, outdoor-29vdc on mnet- swapped o...utdoor boards with another unit-changed address on rotary switches ok-still fooking alarms(have done virgin restart- also the g50 was connected to oudoors 51,58 couldnt detect system 58- refrigerant moniter only showed 51 outdoor 52 bc 1-7 indoors and controllers-couldnt detect system 58- tb7 link from 51-58 ok-mitsi suspect power pack on g50!- any ideas? ta

I doubt the power pack. You dis-connected TB7 (G50) and you still had 6607? Right?
Grouping indoor units with the M-Net controller might be the issue. Has the system had any modifications of late?

install monkey
14-03-2012, 11:08 PM
its been in for 4 yrs and was probably modified 2yr ago when the hotel was refurbished-we took over the repairs etc 8mth ago- dont know if its ever worked properly-as the system still operates with the fault code flashing-doesnt help with a site handyman-sticks his screwdriver in anything!- strange how the outdoor doesnt detect 3 controllers on the system- but the controllers work ok? also theres a few covers off the indoors so someones been poking about

Reffnut
17-03-2012, 10:03 AM
i thought that sw1 1,2,10 only brought up the bc box addresses?

1torr
17-03-2012, 04:59 PM
Thats correct

install monkey
17-03-2012, 09:00 PM
sw 1 ,1 and 10 is indoor unit addresses 2,10 bc box address 1,2,10 remote controllers- i checked this on system 51 and all is displayed remotes,indoors and bc, but not on system 58

JoeAT50A
19-03-2012, 05:14 AM
Hi IM, could you please check outdoor units' SW2-1s all should be ON so that your G-50A will decide the grouping of indoor unit and remote controller.
If SW2-1s are OFF, outdoor unit will decide the grouping.
I think one of the outdoor unit's SW2-1 is OFF position (may be system 58).
Hope this help for this issue.

install monkey
19-03-2012, 09:06 PM
sw2-1 is off( centralised controller) for all 8 outdoors- i checked system 51 and that picked up all indoor controllers,the g50 picked this up- with 51 and 58 connected only 51 exists on the g50, both outdoor pcbs were swapped to see if there was an issue,but still problems with 58

Hi IM, could you please check outdoor units' SW2-1s all should be ON so that your G-50A will decide the grouping of indoor unit and remote controller.
If SW2-1s are OFF, outdoor unit will decide the grouping.
I think one of the outdoor unit's SW2-1 is OFF position (may be system 58).
Hope this help for this issue.

JoeAT50A
20-03-2012, 01:52 AM
SW 2-1 ON for (all) both outdoor units. And register again in G-50A for groups.
RC must shown on the G50A, check all the registered groups one by one.
G01 should shown 001 indoor, 101 remote controller and so on.
Check all 13 indoor units you have.

8749

stufus
20-03-2012, 02:30 PM
As joe says the g50 wont picpk them up if it doesn't know it has to look for them.
Programme all units and initialise G50 again.
Cheers
Stu