View Full Version : condenser fans won't stop running k control mr slim ?



roznic
14-03-2012, 09:32 AM
hi guys, wonder if you could help out? got an old mr slim cassette found a p8 fault on the controller. Checked outdoor unit found the glass fuse on the PCB blown, replaced and condenser fans came on strait away. unit started and is running fine.
but when i turn it off from the controls the condenser fans constantly run!
could it be a problem with the pipe thermistor ? to my knowledge doesn't this control the fan speed/ cycle?

MR Kein
14-03-2012, 10:17 AM
P8 could mean a saftey device worked like HP. Or could be damage coil thermistor.

Grizzly
14-03-2012, 05:47 PM
Hi roznic.

Check out the following.

8714

Abnormality of pipe temperature.
Not my area, but I would suspect maybe a high discharge temp which would drive the condenser fans?

install monkey
14-03-2012, 06:58 PM
or relay on outdoor pcb welded- unplug the 2 fan connectors and test continuity from the fuse to the live out to the fan- isolate it first though

Grizzly
14-03-2012, 10:04 PM
or relay on outdoor pcb welded- unplug the 2 fan connectors and test continuity from the fuse to the live out to the fan- isolate it first though

Thanks for the extra advise its appreciated,well at least from me!
Grizzly.

install monkey
14-03-2012, 10:20 PM
https://rapidshare.com/files/2902456089/mitsi_mr_slim_r22.pdf;
2 dipswitches on the outdoor will give u the coil temp- p8 is outdoor abnormality- ceck for flashing led on outdoor pcb or it will alarm p8 if indoor room temp doesnt change in 15 mins- ie dirty filter - blocked vents- etc

roznic
15-03-2012, 08:03 AM
thanks monkey.

I'll check that next time im round there.
i unplugged the pipe thermistor to see if the fans cycled off but didn't.
I'll try the continuity.