I have a semi-hermatic compressor that when valved off it will not pull into a vacuum. If you cut the compressor off, the low side will jump up to what ever the pressure is on the high side with in less than a minute.The dairy case is keeping temperature but i can not get the SC and SH right on it, and it has higher than normal head pressure for 404A . Would it not pulling a vacuum when you valve it off cause SH and SC issues ? What other problems would it cause ? Thanks for your help

chemi-cool
14-03-2012, 05:15 AM
Broken valve.

You will need to repair it or replace it.

Sandro Baptista
14-03-2012, 10:41 AM
Replace the valve plate

jakb21599
14-03-2012, 12:11 PM
Would the broken valve affect the SH and SC ? Would it affect the low and high side pressures ?

Sandro Baptista
14-03-2012, 01:15 PM
SH does means superheating?
SC does means??...subcooling??

Sandro Baptista
14-03-2012, 01:19 PM
"Would it affect the low and high side pressures ? "

Yes, since it promotes an equalizing tendency (due to internal by-pass). As consequence the low pressure tends to be higher (so the evaporating temperature will be higher » less capacity to the evaporator). Also the discharge superheating will be higher since the suction gas will be more superheated.

jakb21599
14-03-2012, 02:03 PM
SH does means superheating?
SC does means??...subcooling??
Yes SH - superheat. SC - subcooling

Sandro Baptista
14-03-2012, 02:27 PM
yes, my opinion is that superheated is affected. About the subcooling I can see a direct reason to be affected.

Sandro Baptista
14-03-2012, 02:27 PM
I meant the non useful superheated tends to be higher.

padraic
14-03-2012, 10:17 PM
valve plates..!

THE DUDE
08-04-2012, 11:46 PM
Pull the head, there may be more damage than expected....but most likley just a Valve Plate.

mark957
09-04-2012, 10:49 AM
hello
if the oil pressure is good, it is convenient to replace the valve plates.
hello and good luck.

aramis
09-04-2012, 09:12 PM
Broken valves reduce compressor capacity and you cannot adjust well because the components behave as if they were oversized.