PDA

View Full Version : 3 way mix valves



MikeHolm
04-03-2012, 03:07 AM
Guys, I am looking for a good supply of high Cv 3 way mixing valves, 3/4" to 1.5". Controllers need to be compact and run 0/2-10Vdc. I would prefer 24vac motors but 220-240vac will do. Does anyone know of good suppliers other than the usual suspects like Honeywell and Belimo.


Cheers

stufus
04-03-2012, 09:53 AM
Try ESBE Valves
http://na.heating.danfoss.com/Content/2BA65E67-D19F-4950-B675-148878B2FFC8.html
C (http://na.heating.danfoss.com/Content/2BA65E67-D19F-4950-B675-148878B2FFC8.html)heers
Stu

MikeHolm
04-03-2012, 09:07 PM
Try ESBE Valves
http://na.heating.danfoss.com/Content/2BA65E67-D19F-4950-B675-148878B2FFC8.html
C (http://na.heating.danfoss.com/Content/2BA65E67-D19F-4950-B675-148878B2FFC8.html)heers
Stu

Yea, danfoss is usually included with "the usual suspects". Any more thoughts?

nike123
05-03-2012, 12:04 AM
I wouldn't go farther than that! ;)

Magoo
05-03-2012, 04:13 AM
Berkit, I am not swearing [ spell check ] euro so probably expensive. There are wax motors but slow reaction time. I have used Shnieder motorised valves on larger applications, bleedin'expensive though. There was a cheap as chips motorised vav for chilled water we used years ago on perimetor induction units coolers, I will think about the name and get back to your. cheers magoo

MikeHolm
05-03-2012, 12:15 PM
Berkit, I am not swearing [ spell check ] euro so probably expensive. There are wax motors but slow reaction time. I have used Shnieder motorised valves on larger applications, bleedin'expensive though. There was a cheap as chips motorised vav for chilled water we used years ago on perimetor induction units coolers, I will think about the name and get back to your. cheers magoo

Are you sure Berkit is not a swear word? I will look it up but if I mention it to someone and get punched in the face we will need to have a chat...LOL

Bigfreeze
05-03-2012, 02:40 PM
Are you sure Berkit is not a swear word? I will look it up but if I mention it to someone and get punched in the face we will need to have a chat...LOL

Belimo make the best valves out there.

MikeHolm
06-03-2012, 01:30 AM
Belimo make the best valves out there.

Yea, I know but for 1.25" the actuator gets BIG

Bigfreeze
06-03-2012, 06:28 PM
Yea, I know but for 1.25" the actuator gets BIG

Not for the standard 3 way we use (LR230a). But it might be different on the mix valves although I don't see why it should.

chemi-cool
06-03-2012, 06:41 PM
Mike, try here, i have used them [4"] in the past, very reliable.
http://www.buildingtechnologies.siemens.com/bt/us/Products__and__Systems/hvac_products/HVAC_components/valves/Pages/valves_landingPage.aspx

dinhhung
09-03-2012, 11:11 PM
http://www.kele.com/control-valves.aspx

They are very good people to deal with.
Their kele actuator has 5 years warranty.

Just look around their catalog

cool_tech
15-03-2012, 10:51 AM
I always go for belimo if i cant get the original. beimo equipment is good well priced and good variety. helpful in Aus.

MikeHolm
15-03-2012, 09:51 PM
Well, I went with a Honeywell. Not too bad price and good CV.

http://customer.honeywell.com/honeywell/ProductInfo.aspx/VCZML6100
http://customer.honeywell.com/honeywell/ProductInfo.aspx/VC7931ZZ11

Thanks for the help