View Full Version : Copeland csemi wiring diagrams
r.bartlett
29-02-2012, 07:33 PM
Chaps
ot two new compeland semi and neither have a wireing diagram
one is single phase and one is 3
(both should have been 3 )
the single phas has a terminal box labeled L1 L2 L3 so sparks threw in a 3 phase supply (as it was supposed to be 3 phase I can't blame him either)
this is the single phase unit
We are rewiring to single phase but I need to know why there is L1,2,3 and where the other numbered ones go to :-/
I have scanned the web but nothing gives the full details86538654
monkey spanners
29-02-2012, 07:53 PM
Think they use the same box for single and three phase hence L1 L2 L3.... Can only suggest tracing the wiring to the relay and caps that will tell which is L,N and start.
cadwaladr
29-02-2012, 08:08 PM
get in tuoch with who supplied them and demand a diagram!asap.
aramis
29-02-2012, 08:17 PM
You can find the diagram here:
http://www.emersonclimate.com/europe/ProductDocuments/CopelandLiterature/D27.3.1.0909EGF_DK_CAG_(0700-2998109-03)_0.pdf
Black is Run
Common Blue
Start Brown
Hope this helps.
monkey spanners
29-02-2012, 08:38 PM
Found this,
http://www.emersonclimate.com/europe/ProductDocuments/CopelandLiterature/C27.1.7.0909EGF_MC_ZB_PFJ_3154188_0.pdf
Covers scroll model but may be helpful....
Grizzly
29-02-2012, 09:05 PM
Glad to be of assistance RB.
Follow this link as the manual has referances to wiring your units on pages 11 and 25.
http://www.mediafire.com/?n2t15mitleq
Grizzly
Grizzly
29-02-2012, 09:13 PM
Also check your email!
Grizzly
r.bartlett
01-03-2012, 05:22 AM
many thanks to all:-)
jgroberson
05-03-2012, 01:34 AM
Check ohms to establish common start run terminals on 1 ph
3 ph would be the same between phases
Copeland Semi hermetics usually have the diagram on the inside of the compressor top terminal cover plate
or ask your Copeland wholesaler for a Copeland electrical handbook - It gives you all the diagrams
and lists related electrical parts - relays, overloads and capacitors for each model If they still print them in this paperless world
Or register on Emerson/Copelands site as a contractor and download diagrams from there
D.D.KORANNE
13-03-2012, 06:31 AM
3 phase will be part winding ..just check
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.