Does anyone know where I can get spares for an old r407c ac unit. In particular a coil temperature sensor.

Luke.G
25-02-2012, 12:32 PM
make? model? serial?
what coil temp sensor & any values on the sensor??

install monkey
25-02-2012, 07:58 PM
as previously asked, get the resistances at different temps and contact climate ctr and get a titan or electro equivelent as a last resort-i got a sensor for £11 when york wanted £75- as a last resort
also apparently keeble may have spares see link
http://www.google.co.uk/#hl=en&sclient=psy-ab&q=keeble+heating+air+conditioning+ltd&pbx=1&oq=keeble+he&aq=2v&aqi=g1g-v3&aql=&gs_sm=1&gs_upl=457l639l1l4432l2l2l0l0l0l0l109l209l0.2l2l0&bav=on.2,or.r_gc.r_pw.r_qf.,cf.osb&fp=3a9fd4bda99ebf6b&biw=959&bih=402

charlie patt
25-02-2012, 11:39 PM
if its the air thermistor you can use a lg sensor just different plug if its the discharge sensor use the fujitsu discharge sensor of a pre 2006 sensor the plug is the same

Dave Bristol
27-02-2012, 09:14 AM
Sorry for the delay in replying call out is a bitch sometimes.
The unit is badged as a Vent Axia, Model no. for both indoor and outdoor units is WM18N1/1R on R407c and dated to 02/12(2002).
I believe its a rebadged Haier unit Model ref. AS1828ARNA.
I'm after a coil temp sensor ro go into a 6mm pocket, resistances as follows,
16oC 16Kohm, 26oC 9Kohm,30oC 7.4Kohm.
Help thanks