PDA

View Full Version : thermoking container manuals


jamcool
12-11-2005, 09:44 PM
Have a CFII thermoking unit,anyone has a manual i could use,here is the thing.
All the writings on the control is missing have now was of knowing what is what,HELP!!!!!!

ewart
15-11-2005, 03:43 AM
Jamcool you may need to post a photo of this unit.
Ewart

Reeferjon
17-11-2005, 01:13 PM
Hi WHich model is it, what controller...do you have a BM number

ewart
18-11-2005, 10:26 PM
the BM number is 090171 and the serial number is 0324350730, this is jamcool using ewarts log in

Reeferjon
19-11-2005, 01:44 PM
OK, no luck with the BM or S/No...
Its a CFII what model should be M something from 4 to 40....can you identify the controller model

jamcool
19-11-2005, 04:31 PM
i see M19.3 as model number the thing is unit still icing back to the suction line,the charge has not changed read the sensors,coil 3670 ohms,return 3290 ohms,and discharge 3310 ohms I think those are ok,it has 9 relays on it K1 to K9 would like to know which control what also any manuals or wiring drawings that can be found.
ANY HELP WOULD BE GOOD
jamcool

Reeferjon
24-11-2005, 04:20 PM
I have a manual in PDF for you, its 19meg...contactme off list.
John.

canunez
16-05-2006, 06:10 PM
I have a CFII unit and I am looking for a manual. Did you ever find yours? Can you help me?

Reeferjon
17-05-2006, 10:04 AM
please contact me off list.
JOhn.

WBSERVICEFTW
10-10-2007, 12:37 AM
Help,

Does Anyone Out There Have A Service / Operations Manual For A Thermo King Cfii M37.
Container Unit. Or Know Where We Might Be Able To Find One. Any Help Would Be Greatly Appreciated....thanks

C Bagtas
15-10-2007, 10:51 PM
Hi,
just try to check the suction trottle valve or the 3 way valve,before that is i found in our unit,our unit is refrigeration van that we use in aircraft.

spool25
31-10-2007, 04:23 PM
Hello Guys,

I am also looking for Thermo King manuals. The two manuals I am looking for are

Parts Manual for SB-III 30 SR+
Maintenance Manual SB-III 30 & 50
SR+ ”P-IV+

tariqenng
01-11-2007, 07:17 PM
i need thrmoking mechecal rfigertion dia gram any one have please dend me

tariqenng
01-11-2007, 07:19 PM
any one who can tell me about refigertion cyecal about thrmo king

tariqenng
02-11-2007, 12:48 AM
I have a manual in PDF for you, its 19meg...contactme off list.
John.
ok
i willl get the model no

Thermoking.kong
02-11-2007, 01:59 AM
have you tried a thermoking dealer
you will need the unit serial number

also this site wont allow me to mail it to you as its 23 mb

tariqenng
03-11-2007, 01:16 PM
is anyone have service manuals of xmt thrmoking

thermo prince
03-11-2007, 04:59 PM
Hi Tariq Engg.

Are you working for transport company or a service agent there? XMT is an old generation nosemount truck freezer unit from 1970's - early 80's powered by either Onan or Wisconsin gasoline engines.
Abbar in Jeddah and Riyadh may be able to help with manuals and parts.
Some countries 'repower' these with Yanmar or Kubota diesels and continue to run them today.
If Abbar cannot help w/ parts contact me offline. There's a warehouse nearby me where a large inventory of old hard to find parts for XMt, XKW.XRW and NWD stocked.

Its not a 'Container' unit or Reefer unit like CF11/CSR/CRR as fitted on 20'/ 40' ISO ocean going boxes.

Spool 25 - which part of USA do you work and likewise are you working with owner/transport or a repair company?
Did you try local agent or MPLS Hq for these? If you are an owner or in the trade, they would be happy to oblige I'm sure.

REEFER-TEK
25-11-2007, 03:16 AM
I have a full library collection of all makes and models of TK and CTC units in PDF.

I would like to complete my collection with a Deltec Vector and X2 manual if anyone has any of these in PDF to share or email that would be very cool.

If anyone here is looking for anything I probably have it. Including software wintrac 4.6, reefer manager, SR2 diagnostic tester rev3, ibox 5308, dataview dos, optiset 3.26 rev and way to many more to name off here.

Regards R-T

pedrefer
13-04-2008, 01:57 PM
We have a box with XMT-50 now operating as a stationary unit removed from road chasis, powered by 3 phase 230 volt.

I am Looking for a manual and any information in retrofiting to R134a.

absolute-zero
13-04-2008, 03:07 PM
We have a box with XMT-50 now operating as a stationary unit removed from road chasis, powered by 3 phase 230 volt.

I am Looking for a manual and any information in retrofiting to R134a.

Hi pedrefer,

I see your new here to RE, welcome aboard.:)

Why not convert the sytem to (MP66 R401b). The cooling capacity is better and the sytem is more forgiven to this basic conversion.

paulo almeida
13-04-2008, 04:06 PM
go to web site o fdupon and the have refrigerant for conver direc, not need oil poe

best regards

absolute-zero
13-04-2008, 05:18 PM
go to web site o fdupon and the have refrigerant for conver direc, not need oil poe

best regards

http://www.refrigerants.dupont.com/Suva/en_US/products/suvamp66.html

SKOOBY
13-04-2008, 08:55 PM
Yes i agree MP66 is the way to go.May have manual will let you know

micki_kp
03-06-2008, 02:46 PM
I am looking for a wiring diagram for a thermo king some dummy took the wiring harness out of the unit before they were ready to replace it. any help would be grately appreciated.

thermo king
model sll-38 max
b.m
092039
serial # 0518819091
ref
r502 16 lbs
thank you in advance.

Big John
06-06-2008, 10:43 AM
contact Amer Basaeed @Abbar jeddah

micki_kp
06-06-2008, 12:25 PM
do you have an email address?

clivemtk
06-06-2008, 08:27 PM
how old is the version of reefer manager

Brakefield Man
08-06-2008, 03:25 PM
I have a manual in PDF for you, its 19meg...contactme off list.
John.

I understand you have a PDF Manual for Thermking CFII-M40, is it possible to forward me a copy?

Cheers

peterkelly@spxservices.co.uk (peterkelly@spxservices.co.uk)

icecube51
08-06-2008, 03:53 PM
:off topic:why not make a WIKI somewhere on this forum ,where we can drop all kinds of manuals, or schema's from simple split to highly sofiticated units.
so if someone needs it ,he can simply daownload it.;)

its only an idea,
Ice

absolute-zero
09-06-2008, 02:39 AM
:off topic:why not make a WIKI somewhere on this forum ,where we can drop all kinds of manuals, or schema's from simple split to highly sofiticated units.
so if someone needs it ,he can simply daownload it.;)

its only an idea,
Ice

Copyright of proprietary documents can result in lawsuits based on violation of infringements acts.

Tread the waters carefully as big sharks swim here.

A-Z

Reeferjon
11-06-2008, 10:18 AM
What AZ said....

Big John
11-06-2008, 03:14 PM
TP. dont forget that some xmt units had tukomski engines fitted. I think they were for the US market.we used to get a few in jeddah...

Hummer
12-08-2008, 08:16 PM
I'm looking for a refrigeration circuit diagram for a SB-310+ or similar unit with an electronic throttling valve.

Rodolfo Plata
24-09-2008, 12:17 AM
I have a full library collection of all makes and models of TK and CTC units in PDF.

I would like to complete my collection with a Deltec Vector and X2 manual if anyone has any of these in PDF to share or email that would be very cool.

If anyone here is looking for anything I probably have it. Including software wintrac 4.6, reefer manager, SR2 diagnostic tester rev3, ibox 5308, dataview dos, optiset 3.26 rev and way to many more to name off here.

Regards R-T
____________

Would you have among your collection a XMT thermo king service manual? Unbelievably, We have one of those unit still operating.
Regards,
R. Plata

me777
18-10-2008, 01:01 AM
I have a manual in PDF for you, its 19meg...contactme off list.
John.
Hello ,would you please send me somehow that 19MB ThermoKing manuals PDF; have some alarm codes trobleindicator xls for: REEF AL-CODES-list of indicationsalarms and troubleshooting
for:SabroeTNE405D,E ;TNE406 ;tne508/558 ; Carrier 69NT40 521-xx ;69NT40 511-xx ;69NT40 4xx-xx ;Thermo King Controller mP-C ;yP-a ;yP-A+ ;yP-D ;Thermo King CRR-40 ;Seacold Controler CMS 02 ;RMC-Cargo ;DCM9R.....and plenty of other but don't have that Thermo PDF.Thanks

rftvict_vietnam
11-11-2008, 02:14 PM
Copyright of proprietary documents can result in lawsuits based on violation of infringements acts.

Tread the waters carefully as big sharks swim here.

A-Z
hello, I am a new member of the Forum
I approve your opinions.The document sharing is essential for anyone.It will help us more in identifying the problems to which the repair.
I have some documents about reefer container,although not many and update
but it will help those who need.
if anyone should send mail to me.
it's OK
vict_0938007114@yahoo.com.vn
hope to receive cooperation from members
thanks

lsinc1
10-12-2008, 03:21 AM
I have a full library collection of all makes and models of TK and CTC units in PDF.

I would like to complete my collection with a Deltec Vector and X2 manual if anyone has any of these in PDF to share or email that would be very cool.

If anyone here is looking for anything I probably have it. Including software wintrac 4.6, reefer manager, SR2 diagnostic tester rev3, ibox 5308, dataview dos, optiset 3.26 rev and way to many more to name off here.

Regards R-T

Hi,

Is the wintrac software avaiable for download? If so could you send me a link?

Thank you
Tony

zanman
12-12-2008, 12:54 AM
yes we have them- i can fax you what you might need?

Bermejol
01-02-2009, 03:47 AM
I have a full library collection of all makes and models of TK and CTC units in PDF.

I would like to complete my collection with a Deltec Vector and X2 manual if anyone has any of these in PDF to share or email that would be very cool.

If anyone here is looking for anything I probably have it. Including software wintrac 4.6, reefer manager, SR2 diagnostic tester rev3, ibox 5308, dataview dos, optiset 3.26 rev and way to many more to name off here.

Regards R-T
Hi all, I am new here. I am needing all information possible for the Thermo King V-500, MD I And MD II SR.
thanks for your support.
Thanks and good luck.

xtremeoption
02-03-2009, 12:42 PM
kindly sennd me link. Many thanks


I have a full library collection of all makes and models of TK and CTC units in PDF.

If anyone here is looking for anything I probably have it. Including software wintrac 4.6, reefer manager, SR2 diagnostic tester rev3, ibox 5308, dataview dos, optiset 3.26 rev and way to many more to name off here.

Regards R-T

utc/tk foreman
05-03-2009, 04:09 AM
there are so many cf-II units produced, with so many small differences, that you really do need the specific model number to have the right wiring diagram and fix the unit properly.

metricwrench
05-04-2009, 02:33 AM
How do I contact you? I need help(manual)
wrench

I have a full library collection of all makes and models of TK and CTC units in PDF.

I would like to complete my collection with a Deltec Vector and X2 manual if anyone has any of these in PDF to share or email that would be very cool.

If anyone here is looking for anything I probably have it. Including software wintrac 4.6, reefer manager, SR2 diagnostic tester rev3, ibox 5308, dataview dos, optiset 3.26 rev and way to many more to name off here.

Regards R-T

metricwrench
05-04-2009, 03:27 AM
How do I contact you? I need help(manual)
wrench
If I add an email address, would that help?
thanks
wrench====== shadow@harleydeals.net

biopetro
14-04-2009, 09:05 PM
Hello everyone,

I recently bought a used Thermoking CGII M-22 15kw generator. But the controller was toasted due to corrosion could someone help me with a manual for this unit?

Thanks,

TD

utc/tk foreman
16-04-2009, 02:21 AM
Hello everyone,

I recently bought a used Thermoking CGII M-22 15kw generator. But the controller was toasted due to corrosion could someone help me with a manual for this unit?

Thanks,

TD

I think i have a manual, but you prob wont need it. Those boards are really one of the only problems you see with those gens. It corrodes slightly from the box letting moisture in and then it burns itself. I can almost guarantee if you put a new board in it, it will fire up and work fine.

fabio-zinpao
29-04-2009, 04:58 PM
Hello folks!
I need the MP3000 controller manual and the electric diagram. I appreciate if anyone could help me.

HTL10
08-05-2009, 01:10 AM
Hi. I saw your quote and i was wondering if there is anyway you can send me a download of WinTrac 4.6, Refer Manager, Sr2 diagnostic tester rev3. I been trying to get it forever so i would be glad happy. if you can't then it's ok. Thank. please reply

Hai

I have a full library collection of all makes and models of TK and CTC units in PDF.

I would like to complete my collection with a Deltec Vector and X2 manual if anyone has any of these in PDF to share or email that would be very cool.

If anyone here is looking for anything I probably have it. Including software wintrac 4.6, reefer manager, SR2 diagnostic tester rev3, ibox 5308, dataview dos, optiset 3.26 rev and way to many more to name off here.

Regards R-T

HTL10
08-05-2009, 01:11 AM
My email is Haitle10@yahoo.com

Seban
14-05-2009, 08:29 AM
Can you send the manuals at pasqual@poczta.onet.pl

birnahaf
14-05-2009, 12:12 PM
Can you send the manuals at birnahaf@gmail.com

thanx so much!

pulper
10-06-2009, 12:02 PM
Need manual for MD-ii SR 1998.With the
μP-T
MICROPROCESSOR
futuresinger1@gmail.com
thank you so much please send if ya have.

khaos_unleashed
01-07-2009, 07:12 AM
Hello all I also would like any thermo king manuals available just started work for a refrigerated single axle box truck rental company with various models any help would be greatly appreciated. m.morris2008@yahoo.com

agiouto
07-07-2009, 08:16 AM
Good morning.Please i want the manuals from Thermoking reefer container model Magnum 924

agiouto
07-07-2009, 08:18 AM
Good morning.Please i want the manuals from Termoking reefer container model Magnum 924.

reefercontainer@hol.gr

andreiortan
19-07-2009, 08:46 PM
Hello i have o TK SL200 unit and i whood need software wintrac 4.6 from you.if you could send me wintrac.thanks my email is andreiortan@yahoo.com

abbsnowman
24-07-2009, 04:37 AM
Ok, everyone please stop asking for manuals. This is not a library it is a classroom. Offer something before you ask for something. Maybe then we may help?

bruisermac
25-07-2009, 05:42 PM
i agree with abbs...first time ever..hahahaha...post a new thread with specific needs so it doesnt get so confusing!!!

to answer the original question about flooding or iced up suction line we need more info like box temp etc... as long as the compressor is not iced up your ok cause the cfII with open drive and x430 compressors have a throttling valve to prevent damage to the compressor. on the M35 units sometimes you may get frost to the compressor body depends on the conditions inside etc...

hope this helps.

biopetro
27-07-2009, 02:25 PM
I'm still looking for manuals for a Thermoking CGII M-22 15kw generator.

Thanks.

abbsnowman
27-07-2009, 06:50 PM
If you guys want to know why guys get frustrated with the begging that goes on here, take a look at the amount of posts of the guys helping and the guys asking for stuff. The beggers have 3 or less posts. This tells me that they have likely not even introduced themselves let alone contributed.
I have helped alot and am glad to do it but only a select few actualy say thanks let alone offering something back.
Don't chase away the good guys like reefermech by constantly demanding info.
Post a problem so we can provide solutions and thats when I will give you the books.
So Biopetro, keep looking buddy. :D

biopetro
27-07-2009, 07:51 PM
Sorry if I did anything wrong on the forum. As I stated in my original post on April 14 I had bought a used unit and was looking for manuals for it.

Sadly I don't have anything to add to the forum since I don't work in the refrigeration industry. This was the first and only site I found offering manuals. Sorry the the trouble and if I did anything wrong.

abbsnowman
28-07-2009, 05:36 AM
Sorry if I did anything wrong on the forum. As I stated in my original post on April 14 I had bought a used unit and was looking for manuals for it.

Sadly I don't have anything to add to the forum since I don't work in the refrigeration industry. This was the first and only site I found offering manuals. Sorry the the trouble and if I did anything wrong.



Bio, this is the kind of post I would definatly offer help to. You have stated your problem and have formaly asked for help. No offence taken.
Im realy sorry that I only have truck trailer info otherwise I would lend a hand.
Im sure you can apreciate how many people are just coming on and sponging info.
I will put the word out and see if I can get what you need. Is there a specific problem you are having??
Abbs

greg_haun2000
28-07-2009, 05:53 PM
Hey Folks, i'm new to forum. Working on trans reefers in Afghanistan for the troops. need pdf service manual for thermo king mod# CRR-40-800E Ser# A001082207. don,t have much access to any info here in this dustbowl. any help would be great! Thanks, Greg

greg_haun2000
28-07-2009, 06:22 PM
Looking for pdf service manual for thermo king mod# CRR-40-800E ser# A001082207. I working for the troops in Afghanistan and need help please, not much resources here. thanks for any help, god bless the U.S.

abbsnowman
29-07-2009, 04:02 AM
I wish I could help you my friend but I have zero can info. Maybe Bruisermack could help ya out?

reefermechanic
29-07-2009, 08:15 AM
Looking for pdf service manual for thermo king mod# CRR-40-800E ser# A001082207. I working for the troops in Afghanistan and need help please, not much resources here. thanks for any help, god bless the U.S.


Hi greg_haun,

I sending to your e-mail adress..(greg_haun2000@yahoo.com) is it??

see you reefer mechanic..

reefermechanic
29-07-2009, 08:21 AM
Looking for pdf service manual for thermo king mod# CRR-40-800E ser# A001082207. I working for the troops in Afghanistan and need help please, not much resources here. thanks for any help, god bless the U.S.


Hi Greg,

Whats problem???Maybe ı can help you??I m waiting your reply within " all reefer containers problem".I will be in there..

See you.

reefer mechanic.

mmunhoz
03-08-2009, 12:45 PM
I have most of manuals, but please specify what is theexact model M19, M31, M37, etc..Please inform your email and IŽll attach it to you.

GregDogCO
18-11-2009, 08:53 PM
I'm new to this site. I have an I-box but need help communicating with it. In some posts I've read about wintrac flash s/w and other means of communicting with data loggers but not sure how it fits together. Does wintrac s/w run on pc but also need some flash files for proper communication? I'd appreciate any advice and help getting wintrac s/w too. Thanks.