PDA

View Full Version : CRYSTAL ICE AUTOMATIC ICE MACHINES A603 stuck in def cyle



sork
08-02-2012, 01:27 PM
Hi guys
i am working on a chinese automatic ice machine called : CRYSTAL ICE 603A,when plug in the power, the unit runs , but suction pressure drops , then unit shuts down. unplug the power ,few minutes later plug in the same prob. the water side is ok.
i think the unit stuck in def sycle or some sensor is faulty,causing the valve to close, as it is fully automatic, i initiate the automatic reset to no avail, i can not find any source to download fault code or refer to service manual.
i think the manufacturer or suppliers are in hong kong called ypt international ltd,
any help?

Magoo
08-02-2012, 07:34 PM
Could be a contol problem or lack of refrigerant, google ypt international hongkong.

sork
08-02-2012, 08:07 PM
the unit stuck at the end of harvest, i checked ref 404a, the unit stops valve kicks up, i need to download the basics for it, i check the exp valve everything is ok. it is fully automatic, do not know how and where the suppliers are in uk.

sork
08-02-2012, 08:10 PM
crystal ice automatic ice machines CTM603A MODEL, originally chinese , most parts for are are european.

mikeref
09-02-2012, 06:55 AM
the unit stuck at the end of harvest, i checked ref 404a, the unit stops valve kicks up, i need to download the basics for it, i check the exp valve everything is ok. it is fully automatic, do not know how and where the suppliers are in uk. Ice stuck on evaporator or stuck in door so circuit not closed for new cycle? Alignment and possible foreign matter on harvest door making P.C. stop at that point.

sork
09-02-2012, 09:41 AM
no ice no refrigeration takes place, unit starts , immidiatly suction pressure drops to zero, mag vale kick off , comp stops, thst is all. to restart, unplug and plug the power, the above happens.

sork
09-02-2012, 07:42 PM
mikeref you might be right, i took the pc to check, i was thinking it might be the sensors.

sork
11-02-2012, 05:44 PM
i have tried the above no luck.

mikeref
13-02-2012, 02:49 AM
So it locks out on Low pressure. Remove and weigh gas charge. Drier might have fragmented and blocked cap tube(s). I'm not familiar with this brand of ice-maker.

sork
13-02-2012, 09:07 AM
i have change the dryer, recharged, check exp valve, the unit still cutting out on LP switch.

sork
15-02-2012, 04:56 PM
it is a crystal ice automatic ice machine.CTM603A, metering device is tev
when i turn unit on, the waterpump starts and sprays the water to evaporator, then,waterpump stops, compressor starts, suction pressure drops, compressor shuts down.
anyone help???

sork
01-03-2012, 07:49 PM
thanks guys
the unit is mv 306 scotsman , the fault was the the mag switch and the blockage in thge filter dryer. machine was identified by the people in hong kong.

Magoo
01-03-2012, 10:45 PM
Hi Sork.
problem solved thanks for coming back to us.
So is it a Scotsman made in china, rebranded or name badge engineering.

sork
02-03-2012, 08:03 PM
yes absolutely right. the blockage on the orifice of the tev caused confusion plus other minor adjustments.