I have a strange problem....
Chiller is an ultima 400kw with Carel pco3 controller and an additional Carel eev driver. It's a sporlon eev. The system had been diagnosed by a n other with a refrigerant leak and possible eev failure.
Recovering the refrigerant 45 of a 65kg charge came out. Leaks were found and repaired.
System charged with virgin R407c. The system behaved as before. It should be noted the driers were changed and the mesh filter was found very dirty and blocked. It was cleaned and re installed - this was thought to be the problem, but not so.
When this circuit starts (3 scrolls per circuit) evap pressure falls quickly then recovers for a short time (max 4 bar) then quickly falls and fails on lp.
The display shows the valve fully open.
Subcool starts off fine but falls away as it runs eventually leading to 0 degrees subcool.
Again superheat starts off fine but ends up over 24 degrees.
I am changing the valve, but I'm not convinced it is the valve that is the problem. The valve windings checkout fine too. I'm wandering if it could be a problem with the plan driver??
I'll keep this updated as work continues...
Thanks in advance!
Chiller is an ultima 400kw with Carel pco3 controller and an additional Carel eev driver. It's a sporlon eev. The system had been diagnosed by a n other with a refrigerant leak and possible eev failure.
Recovering the refrigerant 45 of a 65kg charge came out. Leaks were found and repaired.
System charged with virgin R407c. The system behaved as before. It should be noted the driers were changed and the mesh filter was found very dirty and blocked. It was cleaned and re installed - this was thought to be the problem, but not so.
When this circuit starts (3 scrolls per circuit) evap pressure falls quickly then recovers for a short time (max 4 bar) then quickly falls and fails on lp.
The display shows the valve fully open.
Subcool starts off fine but falls away as it runs eventually leading to 0 degrees subcool.
Again superheat starts off fine but ends up over 24 degrees.
I am changing the valve, but I'm not convinced it is the valve that is the problem. The valve windings checkout fine too. I'm wandering if it could be a problem with the plan driver??
I'll keep this updated as work continues...
Thanks in advance!