View Full Version : 30RA Scroll AIR – Water Chiller (30RA 160A)
vanphu
01-02-2012, 08:32 AM
Hi everybody,
Present, I used the Chiller "30RA Scroll AIR – Water Chiller (30RA 160A)"
But I don't have the schematic of the this system. If you have them. Can you help me.
I have a problem with this chiller.
When I running this chiller then waiting about 30 second when this have 1 block run and only this block run.
Remain 3 block not run.
I don't know why.
Can you help me.
Thank you very much.
deaklin
01-02-2012, 12:37 PM
hi mate,i commission these carrier chillers regular,the 3rd compressor block on the controller is not in use on the 30RA,it only has 2 comps per circuit!
Grizzly
01-02-2012, 07:16 PM
8593
hi mate,i commission these carrier chillers regular,the 3rd compressor block on the controller is not in use on the 30RA,it only has 2 comps per circuit!
Hi deaklin.
I suspect you know far more about these than me.
However I have to dispute the 2 comps statement as there is a 3 comp per circuit version.
In fact reading my own attachment it would appear the 160 is indeed 2 +2 comps?
That does not mean that Vanpu has such of course.
Grizzly
james10
01-02-2012, 07:44 PM
Some RA's have 4 comps per circuit I would need full model to be sure though
Brian_UK
01-02-2012, 08:34 PM
Or pick up some details from here...
http://eto.carrier.com/lit.asp
vanphu
02-02-2012, 01:22 AM
Hi everybody,
Thank you for help me.
I'm sorry. It have 2 circuit unit: circuit A and circuit B. But each circuit have 2 compressor.
I think it have problem at the Pro – Dialog control.
Tomorrow, The chiller only run 1 compressor.
Today, I tried again. First, the chiller run have 2 compressor then auto shutdown.When I try again its have error then I reset this error and run the chiller again. Its run good (have 4 compressor run)
Grizzly
02-02-2012, 06:06 AM
Hi vanphu.
The fault you reset may be the clue to what is wrong, what was it?
Grizzly
vanphu
02-02-2012, 06:37 AM
Hi Grizzly,
Now, The chiller activities good.
All compressor activities and its not error.
But I don't know the tomorrow what problem?