mikeref
01-02-2012, 08:31 AM
I have an old Zanotti drop in on a freezer room that is giving me grief. No model number available. Single phase compressor, 2 horse power R404a, hot gas defrost. The room external measurements are in metric, 2.4 by 2.6 by 2.4 metres. 150 mm or 6" insulation. Product load is on site pies, pastry, bread and such which goes to the coldroom before being moved to freezer and further chilled to -18*c. Total product load would not exceed 350 kg at any one time.
The catch is, i have looked after this room for around 18 months,and not had the following dilemma.
The system had severe contamination when i first worked on it. Flushed, added a large capacity drier and sucked it dry. (compressor did not have an oil change due to time constraints, which later came back to bite me.) Now, the room fails to go below -12*c, and this is now 18 months later.
All basic checks have been done. ( fans, iceup, clean condenser, door seal, digital temperature reading verses my digital thermometer, gas charge, insulation moisture, evaporator air duct, air flow, drier restriction, digital temp setting, hot gas bypass, doesn't leak at hot gas solenoid....Take a breath.. CPR setting and.. the following:
After reclaiming refrigerant and another change of drier, (this is a cap system BTW,) recharged at .95 KG.
room temp= -8.1
suction= 225 to 240 Kpa, depending on water in burn off tray
Air onto condenser = 35*C
Air off condenser = 44.8 *C
TD across evaporator, only 4.7 *C. Now that is where i've come unstuck!! Why only 4.7*C when i should be getting 6 to 8*C?
My thoughts are: does the compressor have valve problems, or is the ambient + 70 odd percent humidity causing the evap to ice up prematurely over night? I'm stumped on this one :( Mike.
The catch is, i have looked after this room for around 18 months,and not had the following dilemma.
The system had severe contamination when i first worked on it. Flushed, added a large capacity drier and sucked it dry. (compressor did not have an oil change due to time constraints, which later came back to bite me.) Now, the room fails to go below -12*c, and this is now 18 months later.
All basic checks have been done. ( fans, iceup, clean condenser, door seal, digital temperature reading verses my digital thermometer, gas charge, insulation moisture, evaporator air duct, air flow, drier restriction, digital temp setting, hot gas bypass, doesn't leak at hot gas solenoid....Take a breath.. CPR setting and.. the following:
After reclaiming refrigerant and another change of drier, (this is a cap system BTW,) recharged at .95 KG.
room temp= -8.1
suction= 225 to 240 Kpa, depending on water in burn off tray
Air onto condenser = 35*C
Air off condenser = 44.8 *C
TD across evaporator, only 4.7 *C. Now that is where i've come unstuck!! Why only 4.7*C when i should be getting 6 to 8*C?
My thoughts are: does the compressor have valve problems, or is the ambient + 70 odd percent humidity causing the evap to ice up prematurely over night? I'm stumped on this one :( Mike.