View Full Version : TK won't shut down on cycle.



TysonTech
10-01-2012, 08:22 PM
Hello,

I'm working on a 2002 Thermo King SB-300 trailer mounted unit. The problem is that while in cycle mode it won't shut down once it reaches temperature. It simply flips back and forth between heat/cool. I've checked the discharge air and return air sensors and they seem to be working properly. The maintenance manual I have suggests a "air short cycling around evaporator coil". I honestly don't know what that means. Looking for any ideas or an explination of what the manual was describing.

Thank you in advance.

cadwaladr
10-01-2012, 10:21 PM
it could be several things ,alternator,water temperature sensor wiring?

moggy66
11-01-2012, 01:09 AM
I agree with cadwaladr, water temp or alt , check all your setting one must be not reading correctly

gravy258
11-01-2012, 06:18 AM
when its doing the heat/cool thing, what are the battery amps and volts ?
usually its the battery that will stop it cycling off

giath
11-01-2012, 11:01 AM
hi
check cycle sentry relay.......good luck

tkman
16-01-2012, 10:21 AM
Check amps, if it's over 5 amps it won't shut down.

johnatr
20-06-2012, 01:30 AM
I have ran into the same problem and found that the amps on the micro were jumping all over the place. Thought might be a wiring problem, still working on it. Let me know what you find out if you don't mind.